Correct in Assuming 10.1.
Yes I'm in the Clause 9 now. My minimum thickness is going to be 3/16" welded from one side with no backing. I have to write the WPS and qualify the welders. All parameters will fall under the prequalified specifications.
My biggest confusion is this.
-Table 9.13 states the only way to get the CJP qualification is test 6GR per the Figures 9.25 and 9.27. However the note states that You use figure 9.25 and test per 9.27 (corner macro).
- The narrative 9.19 note (6) states you have (2) options: A) take both 9.25 plus 9.27 or B) 9.25 and test per 9.27.
Now, If we go to Table 9.14 it shows that for box tubing (4) side bends and. (4) macros are required. So if (4) of each specimens are required why would they even give the first option of having to take 2 separate test when you are already doing the macro??
- Per the table 9.14 can we not just use the Figure 9.27 for the test and get the 4 each specimens from that?
Am I just overthinking this whole thing entirely??