Your dryer outlet relies on the neutral and ground being connected somewhere, somehow. More recently apliance plugs & outlets are often 4 prong, 2 hots a neutral and a ground. Modern electrical pannels don't connect the ground and neutral busses, EACH BUSS has a ground lead to a rod driven in the ground. You DO NEED a doubble pole breaker if You add a circut. The 16 amps listed on the welder requires a minimum 20 amp feed, that is #12 wire unless unusually long. Your welder needs 2 conductors with ground. There is nothing wrong with running a 3 conductor with ground wire, that enables You to tap out 115 volt if You need it at a later time. #10 wire and a 30 amp breaker is not a problem other than higher cost, and gives flexability for the future. You could hard wire the welder cord right to the breaker, or You could use a 30 amp 3 or 4 prong recepticle and plug. I used a dryer cord on My old farm welder. You can get a recepticle and plug from a welding suply store, a farm store or a good hardware store. Home Depot & Lowes should have the recepticle & apliance cord, maybee the plug. On the welder the green wire is the ground, the other 2 are hot.