Why qualify if only fillet welds are used?
I think you have a point, and I agree with you. My thinking was that if fillets are prequalified in D1.1, Why not D1.4 as well? That was somewhat a gray area for me, but I was told that a PQR was necessary. I didn't clearly see where a PQR was required in Section 6, and as I reviewed Section 1, I understood 1.3.1, which shows ASTM specs. for reinforcing steel.... I understood 1.3.2, which addresses bars not listed in 1.3.1., but the 1.3.3 paragraph is the one that was the sort of gray area to me. It states that "base metals, other than those previously listed, shall be one of the structural steels listed in the latest D1.1".... but it didn't indicate that the base metals in D1.1, when used in combination with any of the reinforcing bars listed in 1.3.1, were prequalified, nor did it indicate that a PQR was required. Maybe the thinking in my situation was that it's better to be safe than sorry, hence the PQR. However I did see where "WPS for fillet welds shall be considered prequalified and exempt from testing" (6.1.2.1), as you've mentioned. It still seems there could be somewhat of a valid argument with a 3rd party inspector who insists that a PQR is needed for bar to structural, but with the omission of any such statement in D1.4, the "WPS for fillet welds shall be considered prequalified and exempt from testing" would apply, as long as the structural base metal is listed in D1.1.
Any further thoughts?