In clause 6.1.1, D1.1:2008 leaves it up to the EOR or the contract docs during the bidding process to specify any NDT/NDE other than 100% visual (per clause 6.9).
Joe,
I think that you are thinking about the thickness where the UT acceptance criteria starts in Table 6.2 and Table 6.3....5/16" - 8"
edit: you can UT thicknesses less than 5/16, but you need your Level III to develope some acceptance criteria (and NDT procedures) for you to accept/reject the indications should you find something.