Gus TX
"Here is my Question: Can these welders’s be giving qualification papers based on their production welds under d1.5? If so or not so, please give me some Ref."
I think you meant to say "given" instead of "...giving...".
My short answer is "NO"! However the tests are essentially the same. The one big difference is that no power tools are allowed in tests given to D 1.5 (Paragraph 5.21.5.1).
The visual inspection criteria acceptance requirements of D 1.1 is actually stricter than D 1.5 (1/8" max reinforcement for D 1.1, VS 3/16" max reinforcement for D 1.5.) The bend test result acceptance requirements are the same. Radiographic Test Results acceptance criteria requirements are the same.
SO! If the original conducting witness and certifier both agree that the original tests for D 1.1 were given under the same constraints as is required in D 1.5 (No power tools), and the test results were evaluated so that the acceptance requirements of D 1.5 were met, they could possibly be persuaded to issue new Welder Performance Qualification paperwork to D 1.5. (Assuming the work record is up to date.)
If the current job was for "Fracture Critical" construction, then further evaluation would be required.
Joe Kane