benno,
I'm going to agree with you due to the Commentary in D1.5 C3.3.4.1 that the intent of the code is for the ends to be free to move until the buttering is completed and then after the joint is dimensionally correct, the final weld is placed....but what can you do after the fact?
Marshall,
UT is not going to show anything other than to say that the material is free of any dis-continuities...stresses will not show their heads until something is stressed above the material's limits and fails.
For future projects....when an inspector finds a root opening of 1.5" when .375" is detailed, he notifies the EOR of the condition....now what? Will the EOR have to come up with a fix?
How does the erector end up buttering both free ends without having access to the other side...the welder will need some sort of dam or run-off tabs to keep the filler from just running off....then try to get a grinder or something behind the joint to shape up the back side of the root so that the backing bar will fit tight against the back side. Naturally, the easiest way is to place a wide backing bar as you described above.
I've seen this situation before but I have never seen where it ever gets resolved to everybody's satisfaction....thus my question.
It usually ends up just like you have described...the field ends up buttering the joint and the final welds are placed...then the job has a black cloud hanging over it with doubts about what will happen at the joint where the root was way too wide.