You provided limited information and asked for an opinion. You got what you asked for.
I apologize if I struck a raw nerve Bill. I have been accused of practicing snow shovel diplomacy before. It served a purpose; it got your undivided attention.
You have a problem and it can cost your employer a lot of money to correct the welds in question. I have been in similar situations, so I can empathize with your plight. The trick is to come up with a solution that is equable to both parties.
You stated that the UT acceptance criteria was Table 6.3 for cyclically loaded nontubular connections. The criteria is very stringent, so it is a safe assumption the Engineers has concerns and considers the connections to be "critical" to the integrity of the structure. It is also a safe assumption that the connections that were not tagged for UT examination were not as critical to the integrity of the structure, but never the less, there are certain expectations on the part of the Owner and the Engineer regarding the soundness of all the welds.
While I assume you took some level of care in preparing the joints that were not subject to UT, I have seen situations where the contractor took the attitude that anything goes if the connections where not UT'd. Back gouging was approached with no regard to whether sound welds were deposited. Hopefully, that does not describe the attitude of the welders or management in your facility.
The fact is the Owner has identified a problem. The Owner is convinced the work is substandard and you have to come up with a solution that will not bankrupt the company.
What I would propose is that the Engineer did not flag certain joints for UT because they are not critical. They need only pass visual inspection. However, they do have to meet all the visual criteria with regards to fit-up, preheat, interpass cleaning, completeness of back gouging, the back gouges are required to comply with a prequalified U-groove or J-groove before welding from the second side, etc. The welders have to employ tabs at the ends of the grooves to ensure sound welds, etc. The contractor has an obligation to ensure those requirements are met. There are quality control measures that are the contractor's responsibility. As a Verification Inspector I typically ask if the contractor has inspection reports available as objective evidence proper quality control measures are in place and the contractor verified those measures were fully implemented; all welds checked to verify the fit up was proper, preheat and interpass temperature were verified, the completed welds were inspected. If there are no inspection records completed by the contractor there is a serious problem. The owner has a reasonable case that until the contractor proves the welds are sound; there is no reason to assume they are sound.
My next step is to visually examine the welds. Did the contractor use tabs at the ends of the grooves? No? Then it is reasonable to grind the ends of the grooves flush with the adjacent members to check the welds for evidence of subsurface incomplete joint penetration, incomplete fusion, and slag inclusions. If there is any evidence of the defects listed, there is cause to employ PT or MT to assess the seriousness of the problem. How far into the joint does the defect extend into the joint? There are two means of determining the extent of the problem: (1) excavate the groove to sound metal or (2) employ UT as an expedient means of assessing the extent of the problem.
I would suggest that it is prudent for the contractor to suggest to the Engineer and the Owner that the contractor will pay for the joints in question to be tested using UT. The contractor should also offer to repair defective welds if the Engineer and the Owner agree to use Table 6.2 as the basis of acceptance or rejection. I would not be so fast to suggest this approach if the contractor had in process and final inspection reports. I would not suggest this if the contractor used tabs and the ends of the grooves exhibited none of the defects listed in the preceding paragraph. I operate under the assumption the contractor took the necessary steps needed to ensure the welds complied with the design drawings and the code. I would default to UT only if it has been demonstrated the contractor did not meet the visual criteria I have outlined. If the welds fail visual examination, it is the contractor's responsibility to demonstrate the welds are sound and comply with D1.1.
If the Engineers agrees that Table 6.2 is appropriate and the connections meet that criteria the problem is solved. The cost is minimal and the Engineer and Owner are satisfied they have a sound structure. If the welds are found to be defective, take it on the chin and fix them. Public relations are an important part of doing business and growing a business. A disgruntled customer has lasting repercussions.
The information provided in the inquiry is very sparse. There are many unanswered questions because the information is not provided in the inquiry. Did the contractor provide in-process inspection? Did the contractor provide any fit-up inspection? Did the contractor verify the groove details complied with the tolerances of figures 3.4? Did the contractor verify the minimum preheat requirements were met? Did the contractor provide any inspections of the back gouged grooves? Did the contractor check to see that the welders were properly cleaning between weld passes? We have no idea of what level of quality control, if any, was provided by the contractor's quality control/quality assurance personnel.
Many people that have not been involved in fabrication and have not performed verification inspections would expect that all of the QC functions mentioned in the preceding paragraph are automatically provided. I find that many contractors provide little if any QC/QA unless there is a verification inspector camped on premises during fabrication. My experience has been that even though the contractor is an AISC certified fabricator, the minimal level of QC is provided only when it is enforced by the Owner. I have volumes of photographs of defective welds that were clearly the result of the contractor not taking the basic steps required to produce acceptable welds. I have encountered several projects were the contractor told the welders interpass slag removal was not required because the FCAW electrode was approved for "multipass". I have had several projects were the welders were using GMAW short circuiting transfer when the WPS specified spray mode transfer with a different shielding gas than that being used. I have many photographs were the contractor provided no back gouging because as he put it, "No one ever inspects those joints."What steps did this contractor have in place to ensure the welds met even the basic requirements of AWS D1.1? We would like to know the whole story, not bits and pieces. Reference was made to Table 6.2, but it was never stated that the "bad" welds passed UT to those lesser requirements.
Rarely is a weld found to be "defective" because of one unacceptable discontinuity. A short story can usually be written about all the reasons why a welded connection was deemed defective. So, I ask, what was the whole story on this project?
It is safe to say that the Engineer is the individual that will have to play the part of Solomon. He will have to weigh the facts and make a determination whether the "defective" welds are "good enough" or whether they will have to be repaired. If an equitable solution is not agreed to, the lawyers and the courts can make the decision, but it will cost more than it will to make the necessary repairs and the contractor involved will suffer more than a sullied reputation when the dust settles.