Dear Sirs,
With respect to the provision 6.15 of AWS D1.1 that just mentions 03 categories of test (including Full Test, Partial Test and Spot Test) and that does not mention the RANDOM Category.
In my project, the specified NDT Extend is belonged to RANDOM Test Category (Such as 20% Random NDT), then I still don't know that the such Extend of Testing is "20% of weld length" or "100% Weld length of 20% of weld joints" according to AWS D1.1?
Please support me to clarify this issue!
Look forward to hearing from you soonest,
Thank you very much for your kind supports,
Best Regards,
Based on AWS D1.1/D1.1M:2010, there is no random inspection/testing.
The extent of testing defined by D1.1 includes Full Testing, Partial Testing, and Spot Testing.
D1.1 specifies Progressive Testing when a weld fails a Spot Test. The code defines what a Progressive Test is. However, when Partial Testing is required, the failed weld is simply repaired. No additional testing is required when Partial Testing specified, i.e., there is no additional repercussion. The Owner must specify Progressive Testing if he wants to impose a consequence for failing a Partial Test. The Owner must also define “Progressive Testing" in the project specification.
It has been my experience that the inspector performing the testing selects the specific joints or locations to be tested if or when the Owner does not.
It is common for codes to provide a framework for testing, but it is up to the Owner's Engineer to provide the level of detail required by the code plus any additional information needed to perform the work. A corollary to the NDT dilemma; a structural design code provides basic criteria the engineer has to take into consideration such as allowable stress, permissible beam deflections, floor loads, etc., but it is up to the engineer to develop a viable design that meets the Owner's needs. In a similar manner, the code provides the basic information about what must be tested, but the engineer must define the extent of NDT (other than visual inspection). Failure to do so is akin to the designer saying, "Put a beam there." without defining the size, length, or type of end connections required.
Best regards - Al