With regard to "multiple cracks on the tube", upon receiving this material from your supplier, before signing the bill of lading, was it inspected to ASTM A335 Specification for Seamless Ferritic Alloy-Steel Pipe for High-Temperature Service? And was this spec. noted on the purchasing documents that "this material must meet A335 criteria" ?
A335 states this in paragraph 7...
7. Workmanship, Finish, and Appearance
7.1 The pipe manufacturer shall explore a sufficient number of visual surface imperfections to provide reasonable assurance that they have been properly evaluated with respect to depth. Exploration of all surface imperfections is not required but may be necessary to ensure compliance with 7.2
7.2 Surface imperfections that penetrate more than 12 1⁄2 % of the nominal wall thickness or encroach on the minimum wall thickness shall be considered defects. Pipe with such defects shall be given one of the following dispositions:
7.2.1 The defect may be removed by grinding provided that the remaining wall thickness is within specified limits.
7.2.2 Repaired in accordance with the repair welding provisions of 7.6.
7.2.3 The section of pipe containing the defect may be cut off within the limits of requirements on length.
7.2.4 Rejected.
Furthermore, you mentioned that "The manufacturer maintains the cracks will not cause any issue. However, client informed that finned tubes will be used in a heater having a design temp of 600 Deg C." Is this something that was a requirement in the project specifications, and if so, was this relayed to the supplier?
I have a copy of this spec I can send you if you don't have it. Just pm your email address.