By -
Date 12-11-2003 02:54
Sir:
Unfortunately, I do not have the 1996 edition of D1.5. Looking at the 2002 edition, however, I see that paragraph 3.6 does not exclude weld terminations. The term “sound” in paragraph 3.12 has to be interpreted to mean that the weld meets the visual and any applicable NDT acceptance criteria, including profile and reinforcement. For the visual acceptance criteria then, Figure 3.3E applies, and effectively prohibits groove welds that are less than flush with the base material.
Paragraph 6.5.4 states, “the Inspector shall examine the work to make certain that it meets the requirements of Section 3 and 6.26. The size and contour of welds shall be measured using suitable gages.”
Figure 2.4 (Details of Welded Joints for C JP Groove Welds) of the 2002 edition also requires for T- and corner joints made without backing that “Groove welds in corner and T-joints shall be reinforced with fillet welds with a leg size equal to or greater than T/4, but need not exceed 10 mm [3/8 in.]. T shall be defined as the thinner of the attaching elements”. It flies in the face of common sense to think that these reinforcing fillets should be applied to groove welds that are underfilled.
Additionally, if we pretend for a moment that the code does not limit underfill at weld terminations, you have other practical problems – where exactly does the weld termination (i.e. the point at which underfill becomes okay) start? How much underfill is allowed? This of course is not defined in the code.
Clearly, you cannot allow underfill at weld terminations.
Hope this helps,
Mankenberg