Mr. David,
If this has happened in a critical area of the structure (i.e. one for which the WPSs required CTOD testing), then I believe you do have a problem if a consumable was used that is not permitted by the appropriate approved WPS for the member in question.
As I mentioned in my previous post, paragraph 5.18.1 of D1.1 states that "temporary welds shall be subject to the same WPS requirements as the final welds". This means everything (filler metal, minimum preheat and interpass temperatures, welder qualification, etc, etc). Though you may possibly be able to use any of the materials listed in Table 3.1 for the temp attachment (once again I urge caution to make sure there are no other requirements somewhere that would prohibit even this), you need to treat it the same as any other designed weld on the structure.
Best regards,
Mankenberg