Up Topic Welding Industry / General Welding Discussion / Welding of Roof Decking @ 24 Degree Angl
- - By MJohnson Date 04-20-2004 15:38
A few years back, we ran into a situation fastening steel roof decking down on an 18 degree pitch. We were working under AWS D1.3-89 code wich stated that an angle over 15 degrees was not in the flat position and therefore could not be puddle welded. We are in the same boat again, except the angle is 24 degrees. As an inspector, I am inclined to say the pitch is too great and it cannot be welded. The newer D1.3 sheetmetal welding code has changed wording that says "the sheet steel and substrate must be approximately flat". I am asking for your opinion as to what you consider approximately flat. The contractor considers it approximately flat and he has a compelling point. Any angle less than 45 degrees could be considered approximately flat because it is a lot closer to flat than vertical. Did they change this provision because of strong arguments that it could be safely welded at a slope? Your opinion of this matter will be greatly appreciated.
Parent - By bmaas1 (***) Date 04-21-2004 20:56
what gage of decking is it and how will you check puddle welds. Do you have an SDI book(steel deck institue)? If less than 20ga. will probably require weld washers.


Brian J. Maas
Parent - By waynekoe (**) Date 04-22-2004 19:36
The flat position is from 0 to 15 degrees, anthing beyond that pitch requires a new WPS and welder requalification, and since puddle welds aren't prequalified, the procedure would have to be qualified by test. See if the Engineer will let them screw the deck down.

Hope this helps. Wayne