Greg,
First you must calculate the Duty Cycle of the load you will be placing on the equipment. That formula is:
DC={(N x t)/(60 x f)} x 100
N = Production Rate (transformer energizations/min)
t = weld time
f = frequency (power line frequency I.E. 60 Hz)
Then calculate the kVA demand of of the load. That formula is:
kVA-demand = (secondary voltage X welding current) / 1000
It is important to rememeber that transformers are rated at 50% DC in a 1 minute integrating period. So, the kVA 50% DC would be:
KVA-demand X sqrt(DC / 50)
Hope this helps!