The figure I gave has a 5% increase above the table you have for an A325 bolt, that you need to prove on the Skidmore gage during pre-installation verification per the RCSC, July 23, 2000.
We use A325 "TC" (Tension Control "F1852") Bolts that are tightened from one side using a gun that holds the spline and turns the nut until the correct tension is achieved and then it wrings off the spline.
You will still need to find a way to keep the bolt from falling out when the connection is being made up in the field, but it would eliminate the need to hold the bolt head from behind.
John Wright
Here is a post from a Materials Engineer on another Forum responding to welding a HS bolt.
Post Below.
"Depending on what standard you reference, and what strength level is required, high strength steel bolts are manufactured from carbon or alloy steels, with carbon content varying from ~ 0.20 to 0.55. In the quenched and tempered form, these alloys provide high strength and good toughness.
Welding involves extreme heating and localized melting which produces the following:
1. Brittle weld, due to the presence of untempered martensite. The untempered martensite is produced because of the rapid cooling that takes place after welding in thick sections.
2. Overtempering of the heat affected zone (HAZ). Again, depending on the chemical composition and strength level, bolts are tempered at temperatures ~ 300-500 C, and this temperature is easily exceeded in the HAZ, which causes local softening.
3. Severe crack sensitivity, as tempered martensite is quite prone to hydrogen cracking and quench cracking.Depending on what standard you reference, and what strength level is required, high strength steel bolts are manufactured from carbon or alloy steels, with carbon content varying from ~ 0.20 to 0.55. In the quenched and tempered form, these alloys provide high strength and good toughness.
End of Post
We have welded HS bolts, with the Design Engineers approval (signed RFI), but they were always in compression not shear.
Couple of Ideas.
1. Weld piece(s) of cold rolled next to the bolt flat to keep bolt from turning, if using turn of nut method, Then mark and tighten as required
2. If snug tight connection only - impact is acceptable
This post is interesting!!!!