I'd like to elaborate on Mr. Austins reply if I may. Don't feel alone. There's always alot of confusion when it comes to this issue. So here is how I interpret B31.3.
If you look at Paragraph 341.4.1(b) states that "not less than 5% of circumferential butt and miter groove welds shall be examined fully by random radiography or by random ultrasonics. They shall be selected to to ensure that the work product of eack welder or welder operator doing the production welding is included. They shall also be selected to maximize coverage of intersecting long seams. When there is an intersecting long seam, 38mm or 1 1/2 in. shall be included in the examination".
The actual extent of NDE should be included in at least one of the project documents. Whether it be the purchase order, the contract, the design package, the project specs., a letter from the client or even the minutes of the kick-off meeting. But the actual extent should be agreed upon by all involved parties "prior" to the commencement of work. This is very important!
B31.3 is ambiguous as to what they mean by 5% of production welds. Is that "ALL" production welds. It should be agreed beforehand as to the percentage of what. % of Isometrics? % of systems? % of daily production? What percentage? 5%? 10%? You also have to consider the difference between field welds and shop welds. Carbon steel systems compared to stainless steel systems and any other exotic materials. You may want to increase NDE on these materials.
Of course it would be ludicrous to examine 100% of all welds or even 10% of each welder. That is more NDE than I care to think about.
You also have to consider the progressive sampling requirements when you have a repair weld. This is clearly spelled out in paragraph 341.3.4.
Another thing you want to look at is Table 341.3.2.
This table addresses the flaws that ASME is concerned with. The first page tells you which flaws are relevant for each method of NDE. These are the defects and the terminology you must use.
For example, B31.3 does not address burn through. So if you see it on a radiograph, what do you do? Ignore it? My opinion is that you evaluate it as root concavity unless your approved RT procedure does address it. That is possible.
You should get a copy of B31.3 and get thouroughly familiar with it. The NDE coverage can get quite confusing on a large project. But yes, par. 340 is a good place to start.
Hope that helps. Feel free to ask for more info if you need it.