Up Topic Welding Industry / Technical Discussions / pitted steel visual inspection criteria
- - By david bean (**) Date 04-20-2009 14:19
I have a piece of 16 x 36 I-Beam with pitted marks every few feet the pits are about an 1/8 inch deep.
Is there a specific place to look for Acceptance Criteria???

Please respond
:)
Parent - By CWI555 (*****) Date 04-20-2009 15:30
look to the material spec first. It should have tolorances for wall thickness. If it's not impinging on T, then you are to the construction code. After that your into project specs, if none of the above conditions are found to be rejectable, then you have to accept it.
Parent - By Joseph P. Kane (****) Date 04-20-2009 19:16
ASTM A-6, Section 9. first.