PA,
Your mention of low service temperature brings to mind demand critical welds in a structure that's designed to resist seismic forces. When this occurs, welds have to be made with a filler metal capable of providing a minimum Charpy V-Notch (CVN) toughness of 20 ft-lb at -20 degrees as determined by the appropriate AWS classification test method or the manufacturer certification, and 40 ft-lb at 70 degrees as determined by the seismic code or another approved method... when the steel frame is normally enclosed and maintained at a temperature of 50 degrees or higher. The lowest anticipated service temperature (LAST) of most buildings is typically 50 degrees, but for structures with service temperatures lower than 50 degrees, the qualification temperature per seismic criteria must be 20 degrees above the lowest anticipated service temperature, or at a lower temperature. GMAW solid wire is exempt from production lot testing when the CVN toughness of the electrode equals or exceeds 20 ft-lb at a temperature not exceeding -20 degrees as determined by AWS classification test methods.
The manufacturer’s certificate of compliance should suffice as evidence of meeting this requirement. Also, structural drawings and specifications are required to indicate the lowest anticipated service temperature of the steel structure, if the structure is not enclosed and maintained at a temperature of 50 degrees.