Since you're dealing with D1.8, it's would be best to write a Non Compliance Report on the situation. This does two things, it documents the situation and formally, brings it to the attention of the EOR. Think of it this way, you're in court testifying about about this situation and the attorney asks you "Why didn't you inform the engineer about this?". What you say next is going to cause you a lot of grief. Just spend ten minutes and fire off the NCR.
Thanks to all.
Dualie, the shop drawings did not address the access holes. Fabricator took it upon himself to make them in the shape you see in the photo.
99205, this item will be addressed with the EOR in writing. I feel the access holes geometry will be brought into compliance with the option the fabricator chose to follow.
eekpod, your statement is my feelings. In the absence of engineering guidance the code is your guide.
jwright650, that cut is taken from D1.1 2010 Figure 5.2, bottom left, “Rolled Shape or Groove Welded Shape” .
When I read D1.8 2009 Clause 6.10 it gives 4 options for all Demand Critical Welds access holes.
Options:
1. D1.1, which will take you to Figure 5.2
2. AISC 360
3. D1.8 Figure 6.2
4. Special Geometry required by Contract Documnets (they don't have)
In a letter they (fabricator) state the holes are in compliance with D1.1. I don't think the holes are in compliance with D1.1 2010 or any of the remaining options. My next move is a NCR to the EOR.
Hopefully, I'm not heading down the wrong path.
I looks like they put the holes in after the welding, or at least enlarged some kind of existing hole. Kinda defeats the purpose of the hole in the first place
>I"t" looks like they put the holes in after the welding, or at least enlarged some kind of existing hole.
Maybe. but....To me, it looks like somebody wasn't happy with the general finish of the access hole and had them use a hole grinder to dress it up.
Yeah, probably so, only got a bit of grinder marks onthe one edge. In any case, it does not meet the code requirements.
The holes were cut using a torch and were very rough. It was mentioned they needed to be smooth and meet the criteria given in D1.8 2009 Clause 6.10 pertaining to Weld Access Holes.
D1.8 does not require the fabricator to poll the welders if the access hole is large enough to perform the welding operation. D1.8 2009 Clause 6.10 states "Weld access holes for all Demand Critical welds shall conform to the following: and it goes on the give the options.
The area where the access hole meets the baseplate at less than a vertical line is of concern to me. In all of the options for access holes given in D1.8 the access holes would have at a minimum a vertical entrance to the baseplate.
from what I remember of the seismic seminar I took on D1.8 about 6-7 yrs ago the reason for the access hole being that shape and configuration is to reduce stress at the access hole during a seismic event(earthquake). That's why it should have been cut before it was welded. In fact if you read other sections of D1.8 there are additional welder certification tests and it requires the welder taking the test to put the coupons together and this is relevant because the welder needs to be trained to understand why the hole is like that and how to make sure its right.
I've been watching this since it was posted and examining my D1.1, 1.8 and AISC Construction Manual as time permits.
Suffice it to say, it would not be allowed on one of my jobs without an RFI confiming the engineer's acceptance. And, I spend enough time on the shop floor and/or out on the field erection site to watch all prep work, fit up, weld out and completed work that it should have been caught before it got welded.
There would be other issues depending upon the WF size, web and/or flange thickness, welding process, welding position, and other factors.
That prep work can be done manually conforming to many options or automatically by computer burn/cope machines. In any finished form it would need to conform to D1.1 Figure 5.2. See also supplemental information and illustrations in the Commentaries of both D1.1 and 1.8. There are still no options resembling the photo.
Have a Great Day, Brent