If the standard or code one is working to states clearly that re-hydrating and/or drying Cellulose type electrodes are not allowed in any of the clauses then I reject - period! Unless the EOR overrules and states in writing that it can be done on that particular job...
How would I know this happening? Well, quite frankly one has to investigate as to whether or not this is happening by stepping back in order to observe and report, ask questions...
And the only way to verify that there is one or the other, or both is going on - in order to prove this is indeed the case, one needs to take samples of welds deposited with the electrodes being used, and then have them analyzed for increased amounts of alloying elements as well as any unusual amount of hydrogen that may have been trapped in the weld metal as a result of using re-hydrated electrodes, and/or drying the electrodes...
Remember that the EWI report is concentrated on very specific low alloy pipeline steel that will usually have a different chemical composition than the grade of steel used in erecting storage tanks so, remember what type of meat we're chewing on here in this discussion...
Plasma, did you write that you bend tested samples from 3 and 4F joints using cellulosic electrodes? What about groove joints?
"I'm not convinced I would reject just because of that incident" The problem doesn't stem from one incident... The conclusions and recommendations written in the EWI report are not based on only one incident, or just from
studying the various field incidents where HAC was indeed found to be from... EWI also validated via testing the findings found @ all of field cases where the various factors that could have caused these failures listed in the report occurred... So they're presenting proven causes for these types of failures...
Now as far as the Lincoln electric report is concerned, it's pretty clear about what they warn pertaining to re-hydrating electrodes in an uncontrolled manner such as dipping the electrodes in a bucket of water... This is from the introduction of the Lincoln Electric report:
"Cellulosic-covered Electrode Storage Conditions – Influence on Welding Performance and Weld Properties R. Weaver and J. Ogborn The Lincoln Electric Company Cleveland, OH
ABSTRACT
Cellulosic-covered electrodes have been used for shielded metal arc welding (SMAW) circumferential welding of line pipe over many decades. They are characterized by electrode coverings containing organic matter. Unlike low hydrogen SMAW electrodes that achieve optimum results at low covering moisture levels, cellulosic-covered electrodes require much higher covering moisture levels for proper operation.
For example, pipe welders have been known to deliberately expose electrodes to the weather, or even dip them in water prior to use. Further, Johnson and Bruce [1] recently suggested that high incidents of hydrogen assisted cracking (HAC) might be associated with low moisture levels in the cellulosic-covered electrodes used.
This suggests further that storage and handling practices based on conventional wisdom in the field may not be sufficient as the industry transitions to more demanding applications and higher strength materials. Consequently, this work was undertaken to develop more definitive information on the performance of cellulosic-covered electrodes for three purposes:
• determine the influence of various storage and handling practices on electrode covering moisture,
• determine the influence of covering moisture on electrode operability, weld metal chemical composition and weld hardness, and -
• develop more definitive guidelines for cellulosic-covered electrode storage and handling practice.
Three different E8010 type electrodes (one E8018-G and two E8018-P1) were subjected to various storage conditions - temperatures from –40°C (-40°F) to 66°C (150°F), and time periods up to 196 hours. As temperature increased there was a tendency for lower electrode covering moisture levels with corresponding increases in weld metal alloy content (particularly Mn, Si, and Ti), increased weld hardness, increased weld strength and higher tendency to HAC. Variations in electrode operation were also noted.
KEYWORDS: SMAW, Cellulosic-covered Electrodes, Covering Moisture, Storage Condition, Weld Strength, Weld Hardness, Chemical Composition, Hydrogen Assisted Cracking
BACKGROUND
A recent paper by M.Q. Johnson and W. A. Bruce [1] dealt with incidents of hydrogen-assisted cracking (HAC) in the welds of line pipe welded with cellulosic-covered electrodes.
A number of topics related to the possible causes for the HAC in the girth welds were discussed. One of these topics was the effect of covering moisture on electrode operation and the resulting weld metal chemical composition and hardness This led to questions about storage conditions and the effect on covering moisture for temperatures between room temperature (24°C (75°F)) and 86°C (186°F) as well as for different lengths of storage time.
Consequently, this work was undertaken to take a closer look at the effects of reduced moisture levels on cellulosic-covered electrode operation and weld performance. Some of these effects are known through practical experience. The changes in operating characteristics are a more globular metal transfer across the arc and a less forceful arc. These changes in welding characteristics were consistent for electrodes that have lower covering moisture content. A possible mechanism explaining the relationship between covering moisture content and arc force could be the very rapid, extreme change in volume as water changes from a liquid to a vapor.
This rapid expansion might be causing metal droplets to travel faster creating more arc force. This rapid expansion could also be causing the molten metal to transfer across the arc as soon as it becomes molten which would result in a fine, spray droplet transfer. Conversely, lower moisture levels would have a lesser amount of vapor expanding which would lead to a lower arc force. It would also allow the molten droplets grow to a larger size before transferring across the arc, yielding a more globular droplet transfer. Field practice supports this idea. It is common practice (although not recommended) for welders to improve the operability of dry electrodes by re-hydrating them in some manner. A few examples of re-hydrating techniques are:
a) leaving containers open to the atmosphere in a humid location,
b) wiping them with a damp rag,
c) dipping the electrodes in water.
The potential problem with re-hydrating dry electrodes in this manner is the lack of control over the amount of re-hydration that actually takes place." Duh!
Then it goes on and on with theories and hypotheses which supposedly explain what, how and why these issues occur... And then we read the conclusions followed by the recommendations (API 1004ish!) which goes like this:
"RECOMMENDATIONS
1. Explore whether covering moisture loss occurs in unopened cans when stored at higher than room temperature conditions or whether it is just an “open product” phenomenon.
2. Explore an increased number of storage temperatures between room temperature and 49°C/120°F to determine at what storage temperature there are no adverse effects on welding operability and mechanical properties.
3. Explore design changes that will retain covering moisture levels more effectively, even when exposed to higher than room temperature conditions.
4. Explore whether electrodes can be designed and manufactured at the “equilibrium” moisture level, so that they are not subject to the variation."
I know just the person to figure this out... He Len Anderson!!! Here's a problem for you to solve and then sell your solution to the highest bidder... Are you interested?
I read both reports and I came to the conclusion that the EWI was much more thorough, and made far more tests than the Lincoln report, and was more in depth, covered all of the angles based on the various methods of testing used and overall, covered a wider amount of all of the various categories listed as well as the different conditions used to come up with their conclusions... The Lincoln report wasn't anywhere near as thorough and was very limited in it's scope...
I mean, how much more empirical does it need to be? The EWI report does include way more variables than the Lincoln report.. I suggest that you re-read this report thoroughly as opposed to just skimming through it like most people do these days