It might be possible if you can get the EOR to approve it. As long as you never ask, the answer will always be "no". As the D1.1 commentary states, “because of the special skills required to successfully execute a CJP weld in tubular T-Y-and K connections, the 6GR level of welder qualification for the process being used is always required”. The commentary goes on to further state “If the contractor wishes to qualify a welder without existing 6GR status, using box tubes, the welder is to weld the 6GR test assembly of Figure 9.25 and Figure 9.26 using either a round or box tube in conformance with the limitations of Table 9.14. In addition, the welder is to pass the corner macroetch test using Figure 9.27 or, if box sections were used, Figure 9.25 or Figure 9.26, by passing a macroetch test on the corner sections of the test weldment.”